I was wondering if someone could help me with clearing up some confusion on water heaters.
Art. 422.11 (E)(3) says to size overcurrent protection at 150%.
Art. 422.13 FPN (120gal or more) and 422.10 says to size branch circuits at 125% based on cont. load.
What are the guide lines here?
I'm Studying for my jmans exam using mike holts book. In this book there are two example ?'s.
1-- What is the max size overcurrent protection for a 45kw 240v water heater--->4500/240=18.75x1.50=28a next size up 30a
2-- What is the calculated load for the conductor sizing and overcurrent protection for a 45kw, 230v water heater?-->4500/230=20ax1.25=25a
When do I use 150% and when do I use 125%? Is it in the question "what is the max..." and "what is the load or min. size..."?
thanks