Given: EEMAX model EX1608T2 208V/2 phase, 16.6KW (This is 2 single phase 208V branch circuits) and the EEMAX unit and the panel board terminals are 75C rated.
Assumptions: Total distance is about 125ft from the panel to the EEMAX, 4 phase conductors in one raceway, non-continuous 100% resistive load (pf=1)
Calculations:
Can someone verify the above calculations?
Assumptions: Total distance is about 125ft from the panel to the EEMAX, 4 phase conductors in one raceway, non-continuous 100% resistive load (pf=1)
Calculations:
- Use 4-#8AWG THHN 90C rated conductors. (Maximum terminal ampacity is 50A @ 75 deg. C rating for EEMAX and panel board).
- Now derating the ampacity due to 4 current carrying conductors in one raceway by 80% = 55X0.8=44A
- At about 125feet, voltage drop is about 7.78V and the circuit current is = 16.6KWX1000/(208V-7.78V)= 82.9A (Also, the voltage drop is 3.74%. No need to up-size the conductor yet)
- Each 208V/1phase circuit will draw approximately (82.9A/2=41.45A) and the #8AWG ampacity is acceptable (44A per step 2 above)
- NEC allows the next higher over current protective device to protect the conductor ampacity which in this case will be a 45A/2pole breaker.
Can someone verify the above calculations?