I have a calculated design load of 155.6KVA feeding a 225KVA, 3 phase, 208delta/120 volt, 12,460 volt primary, delta-wye pad mounted transformer and a 57KVA calculated design load feeding a 75KVA, 3 phase, 208delta/120 volt, 12,460 volt primary, delta-wye pad mounted transformer.
I have been looking at NEC table 310.16 and using an engineering calc calculator. The engineering calc calculator gave me a wire size of all 0's on one calculation and does not match the NEC for the other calculation.
I want to use XLP, 133% concentric nuetral primary underground cable and underground secondary cable for this project.
I get 155.6KVA/(208v)(sq 3)=431.9amps for the first secondary load. This translates to a 225KV transformer, the next size up. The primary amps calculate to 7.2amps.
I get 57KVA/(208)(sq 3)=158.2 amps for the second secondary load. This translates to a 75KVA transformer, the next size up. The primary amps calculate to 2.6amps.
The NEC has various cable types that must be selected from. I am using 60 degrees centigrade which is 140 degrees farenheit) and assuming THHN cable for the secondary, XLP, 133% concentric nuetral for the primary.
I am getting 600AWG secondary cable for the first calc and 1/0 secondary cable for the second calc. using THHN cable and referencing the NEC, although my engineerinc calc calculator gives me 900AWG and all 0s for the next calc (although no option is permitted for type of cable that I see when using the eng. calc calculator).
For primary cable, I can not find 133% XLP concentric nuetral cable in the NEC. to figure out my AWG.
Does someone know how to do the table look up in the NEC for my situation for both primary and secondary cable??
I have been looking at NEC table 310.16 and using an engineering calc calculator. The engineering calc calculator gave me a wire size of all 0's on one calculation and does not match the NEC for the other calculation.
I want to use XLP, 133% concentric nuetral primary underground cable and underground secondary cable for this project.
I get 155.6KVA/(208v)(sq 3)=431.9amps for the first secondary load. This translates to a 225KV transformer, the next size up. The primary amps calculate to 7.2amps.
I get 57KVA/(208)(sq 3)=158.2 amps for the second secondary load. This translates to a 75KVA transformer, the next size up. The primary amps calculate to 2.6amps.
The NEC has various cable types that must be selected from. I am using 60 degrees centigrade which is 140 degrees farenheit) and assuming THHN cable for the secondary, XLP, 133% concentric nuetral for the primary.
I am getting 600AWG secondary cable for the first calc and 1/0 secondary cable for the second calc. using THHN cable and referencing the NEC, although my engineerinc calc calculator gives me 900AWG and all 0s for the next calc (although no option is permitted for type of cable that I see when using the eng. calc calculator).
For primary cable, I can not find 133% XLP concentric nuetral cable in the NEC. to figure out my AWG.
Does someone know how to do the table look up in the NEC for my situation for both primary and secondary cable??