- Location
- New Jersey
- Occupation
- Journeyman Electrician
I was checking over some engineered drawings and found that they have specified #4/0 Cu for a run about 250' with a 100 amp apartment panel and a 100 amp OCPD ahead of the feeder. In using the Southwire voltage drop calculator I come nowhere near needing #4/0 Cu even with a 3% maximum drop and a full load of 100 amps. Voltage is 102/208, 1?. Some shorter runs 175'-200' are calling for #2/0 Cu. Seems like overkill to me unless the calculations are incorrect. Anyone want to take a stab at the EGC size for #4/0?