hmspe
Senior Member
- Location
- Temple, TX
- Occupation
- PE
"Standard procedure" for calculating a residential 400A all-in-one service (internal 200A 40 space panel plus a 200/2 breaker for a remote panel), at least in the engineering offices in the area I've polled, has been to do a dwelling calc per 220-30 (still on 1999 NEC here), show panel schedules, but not do calcs for the individual panels. Recently a plans reviewer rejected a plan set on the basis that a complete calc was required for each panel feeder in addition to the whole dwelling calc (ie, . Since the demand factors that are available for a panel calc are not the same as for the entire dwelling, I'm seeing a number of instances where the total dwelling calc may be only 300A but there's no way to distribute the loads and calc the panels so that each panel is under 200A. I'm getting lots of irate calls from contractors because the equipment costs are significantly higher for an installation with a 400A service with mains only .
How is this handled in other jurisdictions? All comments welcome.