kendrichchan
a 16.75kw rated range have full current value of _______ amps for load calculation purpose? please show how
thanks
thanks
thanks
1 range 16.75= 12+(4.75x.05)=12,2375Look at Table 220.55 and read note #1 and see if you can figure it out. If you can't, post how you tried and the problem you are having and one of us can help you from there.
12375/240=51.56amps
not sure I use the correct number.
Almost right. The 16.75 is a "major fraction thereof" so use 17k. You use the demand in column C which is 8k. You use the amount over 12k to get the demand multiplied by 5%.
17k-12k=5k 5 x.05=.25 8k+(8kx.25)=10k 10000/240=41.66A