We had a calculation in class as follows: "What is the service demand for 5 8KW ranges, 5 10KW ranges, and 5 12 KW ranges"
A question arose when we calculated them, shown below
Column B
5 X 8KVA=40KVA X .45(demand factor) = 18 KVA
Note 2
raising the KW rating to 12KW for the five 10 KW, the calculation is
(5 X 12KW) + (5 X 12KW) = 120KW/10 ranges = 12KW each
demand for 10 12 KW ranges is 25KW
Adding the two demands you get 18KW +25KW = 43 KW
Can the total demand just be taken from column C since they are all under 12 KW? The demand would be 30KW instead of 43KW. I think so.
The question arose was when it was asked "what if one or more ranges were over 12 KW? Would we be required to calculate the demand using note 2 for the ranges over 8 3/4KW from column C, and the ranges below 8 3/4 KW from column B, and add them, as in the first example"? The demand factor is quite a bit larger calculated this way, even if only one range was rated at 14KW, instead of 12KW.
Opinions?
A question arose when we calculated them, shown below
Column B
5 X 8KVA=40KVA X .45(demand factor) = 18 KVA
Note 2
raising the KW rating to 12KW for the five 10 KW, the calculation is
(5 X 12KW) + (5 X 12KW) = 120KW/10 ranges = 12KW each
demand for 10 12 KW ranges is 25KW
Adding the two demands you get 18KW +25KW = 43 KW
Can the total demand just be taken from column C since they are all under 12 KW? The demand would be 30KW instead of 43KW. I think so.
The question arose was when it was asked "what if one or more ranges were over 12 KW? Would we be required to calculate the demand using note 2 for the ranges over 8 3/4KW from column C, and the ranges below 8 3/4 KW from column B, and add them, as in the first example"? The demand factor is quite a bit larger calculated this way, even if only one range was rated at 14KW, instead of 12KW.
Opinions?