calculation method for a duplex?

Status
Not open for further replies.

sparkwell

Member
Location
United States
Hi I recently took my wa. Administrator gen. 01 exam and passed all portions except for the major load calcs. I felt thoroughly prepared until I was ambushed with duplex questions. In which none of my practice exams and books cover. nor are their any examples of a duplex calc. In the Annex D of the 2014 nec code book. My question is which calculation method does a duplex fall under? Single family or multifamily. Article 100 definitions is single family: one family. Duplex: IS Two family. and Multifamily is 3 or more units. Alittle confusing to me on which method to choose. In my exam I worked the question as single family and fell short. Can anyone help me out, thankyou.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Without getting a better idea of the nature of the questions on the test, it will be hard to answer your question. But in general, you calculate the load for each one of the two units as though it were a stand-alone single family dwelling unit. Then if they ask for the service load to the duplex as a whole, you add all the loads for both units, and apply whatever demand factors are available. For example, let's look at 220.53. If each unit has a dishwasher, a garbage disposal, and a trash compactor, then you can't take advantage of the 75% demand factor when you are calculating the unit. But when you calculate the duplex, you have a total of 6 fixed-in-place appliances, and you can apply the 75% demand factor.

That is about as far as I can go, without more information about the test question. I hope you do better on your next attempt. It took me two attempts to pass my Administrator test. But that was (gulp! :eek:hmy: ) 15 years ago. The test will have changed since then.

Welcome to the forum.
 

sparkwell

Member
Location
United States
General method calc. for duplex?

General method calc. for duplex?

Thank you both for your earlier responses. A major Family Emergency has delayed my reply time. With your advice I have figured the optional method for a duplex but am still struggling with the general. Can you give me some pointers on where I may be going wrong here on this made up calculation? Im really looking for the proper steps to take.

Size the minimum service for the following duplex. Each unit includes the following

1500sq.ft. living area
2-5 hp single phase 240v A/C
15 kw space heat 240v
14 kw range 120/240v
4 kw water heater 240v
5 kw clothes dryer 120/240
2 kw dishwasher 120v
1/2 hp compactor 120v
1/3 hp disposal 120v


my solution:
1500 sq.ft. x 3va 4500va
small appliance 2 x 1500 3000va
laundry 1 x 1500 1500va
9000va


Table 220.42 Ltg. demand:
first 3000va @ 100% 3000va
remaining 6000 @ 35% 2100va
5100va

5hp A/C 28a x 240v=6720va x2=13440
compare to 15kw space heat (omit a/c) 15000va

w.h 4kw x75%= 3000va
d.w kw x 75%= 1500va
comp.1/2 hp 9.8a x 120v=1176 x 75%= 882va
disp.1/3 hp 7.2a x 120v=864 x 75%= 648va

5kwdryer 5000va


14kw range table 220.55 column c 11x10%=12100

largest motor comp. 1176 x25%= 294va
total 43524va/240v=181.35a

I feel like I should be multiplying by 2 or something somewhere to account for the other unit please help.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I quoted in red but I didn't check everything

Thank you both for your earlier responses. A major Family Emergency has delayed my reply time. With your advice I have figured the optional method for a duplex but am still struggling with the general. Can you give me some pointers on where I may be going wrong here on this made up calculation? Im really looking for the proper steps to take.

Size the minimum service for the following duplex. Each unit includes the following

1500sq.ft. living area
2-5 hp single phase 240v A/C
15 kw space heat 240v
14 kw range 120/240v
4 kw water heater 240v
5 kw clothes dryer 120/240
2 kw dishwasher 120v
1/2 hp compactor 120v
1/3 hp disposal 120v


my solution:
1500 sq.ft. x 3va 4500va
small appliance 2 x 1500 3000va
laundry 1 x 1500 1500va
9000va

I would multiply this by 2 and then take your 100%/35%

Table 220.42 Ltg. demand:
first 3000va @ 100% 3000va
remaining 6000 @ 35% 2100va
5100va

5hp A/C 28a x 240v=6720va x2=13440
compare to 15kw space heat (omit a/c) 15000va

w.h 4kw x75%= 3000va
d.w kw x 75%= 1500va
comp.1/2 hp 9.8a x 120v=1176 x 75%= 882va
disp.1/3 hp 7.2a x 120v=864 x 75%= 648va

5kwdryer 5000va


14kw range table 220.55 column c 11x10%=12100

This is not correct. Table 220.55 says to take 8kw as the load for any range over 12 and add 5% for each kw greater than 12. 14-12= 2kw 2x 5%= 10% 8x 1.1=8.8kw

largest motor comp. 1176 x25%= 294va
total 43524va/240v=181.35a

I feel like I should be multiplying by 2 or something somewhere to account for the other unit please help.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Did you get the mike holt spreadsheet I sent you? It has all kinds of calculations- single family, multifamily, duplex, dryer, ranges, schools, etc. Check your spam if you didn't get it.
 

sparkwell

Member
Location
United States
duplex calcs

duplex calcs

yes I did receive the spread sheet. Thank you for that and the quotes as well. I feel these will be very helpful in my quest...your time is very much appreciated thank you.:D
 

sparkwell

Member
Location
United States
duplex calc. range demand

duplex calc. range demand

regarding your correction on my range demand. I used 11kw because I counted 2 14kw ranges due to having a duplex. should I have only counted 1 range?
 
Status
Not open for further replies.