I am trying to determine if there is any relationship between NEC 430.122 - pertaining to treatment of VFD feeder loads and 430.24 - determining motor group feeder load for an MCC.
An MCC is to be populated with both FVNR starters and non bypassed VFDs.
To determine the total load for the MCC does NEC 430.122 come into play or do I just use connected motor FLC as directed by 430.24 items 1 & 2?