I'm upgrading my outside 100 amp panel to the new heat pump an wanted to calculate if I will need a 60 or 50 amp double breaker on the 9.5 kw heat kit.
I have #6 wire .The information on unit/kit says
mca is 49 ,mop is 50 .
.I saw in another post someone spoke on the math % calculation an it looks like I'd need 55 or 60 if 125% applies ---?
I saw this ~
10,000 watts divided by 240 is 41.6 amps. This is a "continuous load" so the wires must have an ampacity of 125% of 41.6 amps, which is 52 amps.Apr 30, 2008
I have #6 wire .The information on unit/kit says
mca is 49 ,mop is 50 .
.I saw in another post someone spoke on the math % calculation an it looks like I'd need 55 or 60 if 125% applies ---?
I saw this ~
10,000 watts divided by 240 is 41.6 amps. This is a "continuous load" so the wires must have an ampacity of 125% of 41.6 amps, which is 52 amps.Apr 30, 2008