Hello Mike I getting ready to supervisor test in Oregon. Can you help me to figure out in this practice question.
I have office space lighting is separate 277 volt.
208 v load include
General use receptacle, Computer receptacle, Copy machine receptacle.Total load is 115000 VA
I have to size transformer, panel and secondary wire size to feed that panel.
To size secondary overcurrent device* (panel) for transformer you have to multiple by 1.25, but is it work in this situation?*
For 115000 VA I need to use 150 kVa transformer
if you size panel by load not by transformer
115000/(208?1.732)= 319 amp So breaker size will be 350 amp or I have to 319 ? 1.25=399 amp and breaker will be 400 amp. Can you explain me what the right way thanks.
I have office space lighting is separate 277 volt.
208 v load include
General use receptacle, Computer receptacle, Copy machine receptacle.Total load is 115000 VA
I have to size transformer, panel and secondary wire size to feed that panel.
To size secondary overcurrent device* (panel) for transformer you have to multiple by 1.25, but is it work in this situation?*
For 115000 VA I need to use 150 kVa transformer
if you size panel by load not by transformer
115000/(208?1.732)= 319 amp So breaker size will be 350 amp or I have to 319 ? 1.25=399 amp and breaker will be 400 amp. Can you explain me what the right way thanks.