Building has central heating unit of 150kw, 480volt, 3 phase fixed electric heat. What is minimum THHN branch circuit conductor required? I get 2/0 copper. Is this correct?
Building has central heating unit of 150kw, 480volt, 3 phase fixed electric heat. What is minimum THHN branch circuit conductor required? I get 2/0 copper. Is this correct?
Temperature Limitations. The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
Branch-Circuit Sizing. Fixed electric space-heating equipment shall be considered continuous load.