noeernlat
Member
- Location
- Washington State
I need a little help understanding something here. I have a 3 phase 125A panel listed on the plans as being fed by 1 1-2" Conduit containing (4) 1AWG conductors and (1) 6AWG conductor. The calculated load for this panel is 14.8 Kva, if I'm correct this equates to a calculated load of 41 A. Now, I assume i have to derate due to 4 or more current carrying conductors which is 1 AWG (90deg Column) 150 X.80= 120A. Am I permitted to supply this gauge wire to a 125A panel even if the calculated load is 41A?? Im thinking I would need to run 1/0 Conductors. Thanks!