answer
answer
common question on the Icc test. The question is for a 3-1/2 rigid metal conduit with 4 - 350 kcmil thwn conductors. to answer this question, just take the total area of the conductors which is 2.0968 square inches per chapter 9 table 5 and then divide that by the total area of the conduit which is 10.01 square inches per chapter 9 table 4 and you get .209. move your decimal over 2 places to get a % and you see that the correct answer is 20.9% or on the test it is 20-30% Do NOT use Chapter 9 Table 8 for conduit fill you will get the wrong answer. You must use Chapter 9 Table 5 for conduit fill. Table 8 does not include insulation.