Hi,
I wanted to get a consensus on this topic because I have read conflicting arguments on how to calculate total load on a feeder using existing metering data and new load. Let's assume we have done a 30 day load study and have and multiplied the load times 1.25 as stated in the code, NEC 220.87. I believe this is agreed upon and confirmed by everyone. The confusion occurs when adding in new load. Do we (assume load is continuous):
A. Take 1.25 of the continuous load + (1.25 X existing load) < breaker rating
B. Take continuous load + (1.25 X existing load) < breaker rating
C. Take continuous load + (1.25 X existing load) < 80% of breaker rating
Honestly I see (C) done more often than not on electrical drawings. Essentially (C) is the same as:
[Take continuous load + (1.25 X existing load)] x 1.25 < breaker rating
This doesn't really make sense,but the city usually will freak out if they see you have done (A) and show your final amperage greater than 80% of the main breaker. So I usually do C. Problem is I feel like we are being overly conservative and the code doesn't really require this.
Thoughts?
I wanted to get a consensus on this topic because I have read conflicting arguments on how to calculate total load on a feeder using existing metering data and new load. Let's assume we have done a 30 day load study and have and multiplied the load times 1.25 as stated in the code, NEC 220.87. I believe this is agreed upon and confirmed by everyone. The confusion occurs when adding in new load. Do we (assume load is continuous):
A. Take 1.25 of the continuous load + (1.25 X existing load) < breaker rating
B. Take continuous load + (1.25 X existing load) < breaker rating
C. Take continuous load + (1.25 X existing load) < 80% of breaker rating
Honestly I see (C) done more often than not on electrical drawings. Essentially (C) is the same as:
[Take continuous load + (1.25 X existing load)] x 1.25 < breaker rating
This doesn't really make sense,but the city usually will freak out if they see you have done (A) and show your final amperage greater than 80% of the main breaker. So I usually do C. Problem is I feel like we are being overly conservative and the code doesn't really require this.
Thoughts?