Need to calculate the size trough needed for 16-500kcmil (line and load from ATS) 10 foot distance.
376.22 tells me that the sum of the cross sectional area of all contained conductors at any cross section of a wireway shall not exceed 20% of the interior cross-sectional area of the wireway.
My calculations for 16- 500kcmil (.7073 x 16) = 11.30 total if I divide that by 20% I come up with a cross sectional area of 56.60
How do I calculate the cross section of the trough size I would need?
376.22 tells me that the sum of the cross sectional area of all contained conductors at any cross section of a wireway shall not exceed 20% of the interior cross-sectional area of the wireway.
My calculations for 16- 500kcmil (.7073 x 16) = 11.30 total if I divide that by 20% I come up with a cross sectional area of 56.60
How do I calculate the cross section of the trough size I would need?