It only has exisitng lighting. I am taking a stab at the calculations
This is Existing at The warehouse is basically empty.
22-1000w fixtures lighting EXISITNG
20-120v recptacles ( new ) Non cont ADD
4- welding 12.3kw each 230v 33a 3p Non ADD
air compressor 230v 25a 3p motor load ADD
MORE TO BE ADDED
Attempt at calculation (Let Me know What I am doing wrong Please )
general lighitng 22,000va
receptacles 20x180va = 3600va
compressor motor 25ax 230v x 1.73 = 9,930VA
Welders 12.3 VA x4 = 49200VA
Total VA = 84730/240x1.73= 204A
The general lighting is only thing original. I would like to also figure load. Am i going in right direction with Calculations
Just off the top of my head:
Lighting is first figured by sq ft per T220.12(?) and then compared to actual.
Actual will be off ballast info, not bulb wattage.
Largest is used and is considered continuous.
Yeah, 180VA per duplex.
Lighting and receptacles then get calced per 220.42 and maybe 220.44 also. Depends.
Welders usually have duty cycles allowing for a reduced calc, but 4 x max works.
Compressor-is 25A FLA or MCA?
These are just the first things that popped into my head.