Can we use demand calculations NEC 220.82 if incoming service to the site is 208, 3phase, and then feeding different apartments with 208V, 1 phase?
 
Can we use demand calculations NEC section 220.82 for each dwelling unit, if incoming service to the site is 208, 3phase, and then feeding different apartments with 208V, 1 phase?
 
220.82 is only for one dwelling unit. For the service load for two or more dwelling units you use 220.84.
 
Can we use demand calculations NEC section 220.82 for each dwelling unit to feed with 208V, 1 phase, while incoming service to the site is 208, 3phase?
220.82 is only for one dwelling unit. For the service load for two or more dwelling units you use 220.84.
Yes I am applying 220.82 to each dwelling unit separately. I think 220.82 indicates it can be applied to a single dwelling unit whether it separate building or in a multifamily dwelling
 
So my question is still there can we apply 220.82 while site itself has 208, 3ph (each apartment will have a feed 208, 1 phase) incoming service?
 
So my question is still there can we apply 220.82 while site itself has 208, 3ph (each apartment will have a feed 208, 1 phase) incoming service?
Yes your referring to a 'open wye', many places in the code refer to 'open wye' systems, such as

Article 220 220.61(C)
"a 3-wire circuit consisting of 2 ungrounded
conductors and the neutral conductor of a 4-wire, 3-phase,
wye-connected system"

And a slight variation in Article 310.15 (E)(2), 400.5(A), 520.44
"a 3-wire circuit consisting of two phase conductors
and the neutral conductor of a 4-wire, 3-phase, wye-connected
system"

Open wye is often confused with with split phase systems where neutral current can sum to 0.
the NEC should really add a definition of open-wye to assist code users in understanding these systems, and the way its referenced technically but unintentionally exempts a open wye configured transformer bank
 