(edit: first) picture is displaying what I would call a "Chicago" threeway. You'll notice the neutral is used in the switching, which is illegal by Article 404.
The smaller pictures to the bottom of the whole picture are details of the boxes.
On the power side, the power is the common, and you have two-wire travellers between switches. (Otherwise, you'd have three-wire running between threeways, right?)
On the switchleg side of the threeway system, you have a dilemma. Since you only have two travellers with no neutral, you have no source of neutral. Therefore, you would have to steal a neutral from somewhere else.
In the picture above, I have pulled power around the room for receptacles, and ended up in the "Switchleg" box with power. Since the supply for the threeway is on the same circuit, it works. If you try to steal a neutral from a different circuit on the same phase, backfeeding may occur. Stealing from another circuit from a different phase could cause backfeeding when the switch is off, maybe. I think I've run into that before.
Notice, you're not switching a neutral with a California threeway. The white wire is ungrounded, and needs to be reidentified per 200.7(C)(2).
Hope that helps.