How's it going, I have been studying for my California State exam and recently took a practice test supplied by the testing agency.
There were a couple questions that I was hoping you could help me out with. I reviewed the material I have from Mike Holt and did some digging around online for similar questions and couldn't find anything. Any help would be appreciated.
Question 1:
-A 3-hp pump is installed 220 feet from the 220-volt main service. What is the voltage drop when using 12 AWG solid wire?
I have been reviewing the voltage drop calculation material and can't seem to find anything similar to this question. They don't give you the current which makes it confusing to me. I'm not sure which type of equation I should be using.
Question 2:
-A feeder supplies a continuous lighting load of 45 amperes and a single motor load of 30 amperes. What is the ampere rating of the feeder?
My answer: 86 amps
Correct Answer: 94 amps
I used code section 215.2(A)(1)(A) and am not quite sure what I missed.
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(1) General. Feeder conductors shall have an ampacity not
less than required to supply the load as calculated in Parts
III, IV, and V of Article 220. Conductors shall be sized to
carry not less than the larger of 215.2(A)(l)(a) or (b).
(a) Where a feeder supplies continuous loads or any
combination of continuous and noncontinuous loads, the
minimum feeder conductor size shall have an allowable
ampacity not less than the noncontinuous load plus
125 percent of the continuous load.
Question 3:
-Approximately how many kilowatts are used by a three-phase, 480-volt ac motor that draws a current of 52 amperes and has a power factor rating of 88%?
I'm not sure what equation to use for this one either.
Thanks again,
Mike
There were a couple questions that I was hoping you could help me out with. I reviewed the material I have from Mike Holt and did some digging around online for similar questions and couldn't find anything. Any help would be appreciated.
Question 1:
-A 3-hp pump is installed 220 feet from the 220-volt main service. What is the voltage drop when using 12 AWG solid wire?
I have been reviewing the voltage drop calculation material and can't seem to find anything similar to this question. They don't give you the current which makes it confusing to me. I'm not sure which type of equation I should be using.
Question 2:
-A feeder supplies a continuous lighting load of 45 amperes and a single motor load of 30 amperes. What is the ampere rating of the feeder?
My answer: 86 amps
Correct Answer: 94 amps
I used code section 215.2(A)(1)(A) and am not quite sure what I missed.
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(1) General. Feeder conductors shall have an ampacity not
less than required to supply the load as calculated in Parts
III, IV, and V of Article 220. Conductors shall be sized to
carry not less than the larger of 215.2(A)(l)(a) or (b).
(a) Where a feeder supplies continuous loads or any
combination of continuous and noncontinuous loads, the
minimum feeder conductor size shall have an allowable
ampacity not less than the noncontinuous load plus
125 percent of the continuous load.
Question 3:
-Approximately how many kilowatts are used by a three-phase, 480-volt ac motor that draws a current of 52 amperes and has a power factor rating of 88%?
I'm not sure what equation to use for this one either.
Thanks again,
Mike