California Title 24 130.5b Disaggregation

Status
Not open for further replies.

raberding

Senior Member
Location
Dayton, OH
Occupation
Consulting Engineer
so...We have a roughly 2500sf restaurant. 3 RTUs (9 ckts), normal led lighting (maybe 8 ckts), some exterior stuff (site lights, signs, drive-thru equip...6-8 ckts), and lots of kitchen equipment. Kitchen equip will take about 66 ckts.
400A, 208/3 service. Looking into the BEST way to segregate HVAC/Lighting/Equipment loads.

I'm thinking we start with a 400A, 42 (for kit equip) with feed thru lugs to a 400A split bus (30/12) that feeds Kit equip (30)/RTUs(12).
Use a 60/3 from the first 400 to feed a 100A/24 ckt lighting/exterior panel.

I think that satisfies the T24 requirements... But, is there a less costly/easier/simpler way?

thanks!
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Have you reviewed the tables?
You don't need to install the RTU's just that you can in the future.

All you really need is separate panels that have the capabilities to have some smart sensors like CT's installed at a later date for metering.
 