California Title 24 requirements

Status
Not open for further replies.
Does California Title 24, or any other applicable code, require the light and the exhaust fan to be switched separately for a bathroom ceiling unit? Would this bathroom ceiling unit light be required to be controlled by a dimmer? And, finally, would AFCI protection be required if installing a new bathroom ceiling fan/light unit required extending a lighting circuit?
 
Does California Title 24, or any other applicable code, require the light and the exhaust fan to be switched separately for a bathroom ceiling unit?

The electrical code does not require that. There might be something in the energy code.

Would this bathroom ceiling unit light be required to be controlled by a dimmer?

I very much doubt that.

And, finally, would AFCI protection be required if installing a new bathroom ceiling fan/light unit required extending a lighting circuit?

If it's extended 6ft or more then yes.
 
Does California Title 24, require the light and the exhaust fan to be switched separately for a bathroom ceiling unit?
Yes

CEC-CF2R-LTG-01-E (Revised 10/16)

150.0(k)2B: Exhaust fans are switched separately from lighting systems, or can be switched OFF in accordance with EXCEPTION.

Would this bathroom ceiling unit light be required to be controlled by a dimmer?
No
150.0(k)2J: In bathrooms, garages, laundry rooms, and utility rooms, at least one luminaire in each of these spaces are controlled by a vacancy sensor.

And, finally, would AFCI protection be required if installing a new bathroom ceiling fan/light unit required extending a lighting circuit?
See 2017 NFPA-70 210.12(A)
 