overkill94
Member
- Location
- California
Just did an inspection on some cam-lok panels - basically a power distribution unit for when they want to do load bank testing. It's rated at 416 Volts, 4000 Amps, 3-Phase and uses copper busing in the panel. A few questions:1. They come across with two 8" x 1/4" bus bars per phase but then split that between two sets of two 5" x 1/4" bus bars split between the cam-lok connectors (13 of them rated 400 Amps each). They claim that each pair of 5" x 1/4" bus bars are good for 3,000 Amps but according to Table 23 in UL 891 it's only 1,000 Amps per square inch which would be 2,500 Amps and thus unable to handle the 2,800 Amps maximum that the part with 7 connectors would be rated for.2. The bolts connecting the connectors to the bus bars do not have any threads showing after the nut. I've always been told you need at least two full threads showing but can't find a code reference supporting that. Is this just a general engineering practice or is it stated somewhere?3. Is there a UL standard dealing with this sort of installation? I used the basic principles for bus bars from UL 891 but this isn't really a switchboard. UL 1640 - Portable Power-Distribution Equipment is the closest I could find but this is definitely permanently installed.Thanks!