Bjenks
Senior Member
- Location
- East Coast of FL
It seems I am getting contradictory advice on surge protection for security cameras mounted on buildings or poles. The job I am working on now has a COAX video feed and 24VAC (I don't see any EGC coming in to the camera). Most SPD companies who address this situation have a device with an IN/OUT BNC and Pos/ Neg. AC connection forming what IEEE calls a Surge Reference Equalizer . Then a big ground lug for connecting to the ?ground.? Typically these cameras are more than 20ft from a GEC.
Here is where I am confused. All of the manufactures I talked to said just run a ground conductor straight down to a ground rod and connect the other end to the ground lug of the SPD. I asked about running a GEC to connect the ground rod to the building GEC and they all said it is not needed. They say this is because there technically isn't a connection to the pole ground rod except during a few nanoseconds of a surge. Would this be a NEC violation of not interconnecting grounding systems or is this different since there normally isn?t a connection? If I also have surge protection where the cables enter the building it looks like article 820 is requiring me to ground the shielding, but I am putting surge protection there and don't believe the SPD will be actually grounding the shield but putting a SPD between it. Is that a violation? Finally, if I do have to interconnect ground rods it seems the requirements of 820 require a #6 connection which doesn?t make sense since the SPD to Rod connection is only #14.
Here is where I am confused. All of the manufactures I talked to said just run a ground conductor straight down to a ground rod and connect the other end to the ground lug of the SPD. I asked about running a GEC to connect the ground rod to the building GEC and they all said it is not needed. They say this is because there technically isn't a connection to the pole ground rod except during a few nanoseconds of a surge. Would this be a NEC violation of not interconnecting grounding systems or is this different since there normally isn?t a connection? If I also have surge protection where the cables enter the building it looks like article 820 is requiring me to ground the shielding, but I am putting surge protection there and don't believe the SPD will be actually grounding the shield but putting a SPD between it. Is that a violation? Finally, if I do have to interconnect ground rods it seems the requirements of 820 require a #6 connection which doesn?t make sense since the SPD to Rod connection is only #14.