EZ Generator Switch
Member
551.71 states 20a 125v outlet for every site.....So in needing a 50 /30 set up for pull thrus a GFCI would be needed also >>>does the outlet (GFCI protected) on the outside of each RV cover this? Considering the only time it would be used is when someone is on that site. We want to install 50/30 units with no 20a GFCI due to the constant replacement issues with these outlets. I have been a Master Electrician a long time and I have never seen GFCI?s go bad like I have in this campground. Almost every single one has been changed at least once...oddly enough they don't get used that much. Almost every unit including pop ups has a GFCI outlet built in and mounted outside why would this not be acceptable...or is this the Authority having Jurisdiction makes the decision? also same article states "Additional receptacles shall be permitted for the connection of electrical equipment outside the RV???" Sounds like its optional ? Another thought >>551.73 calculating loads. 50 amp = 9600 watts and no mention of adding 2400 for each 20 amp GFCI...
Your thoughts?
Your thoughts?