can 120 and 277 occupy the same raceway

Status
Not open for further replies.
They can provided all the parameters are in place. See 300.3(C).
Also note 200.(6)(D) & 210.5 (C)
 
As long both insulations are rated for the maximum voltage applied to the cables, in this case 277volt THHN and the most commons insulation are 600 volt rated .
 