C chriskellaway Member Location virginia Jan 28, 2013 #1 can 120 and 277 occupy the same raceway in not where does it say in the codebook
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 28, 2013 #2 They can provided all the parameters are in place. See 300.3(C). Also note 200.(6)(D) & 210.5 (C)
donselec Senior Member Location Aurora, CO, USA Jan 28, 2013 #3 Yes, generally all conductors in a raceway have to be rated for the highest voltage.
D DARUSA Senior Member Location New York City Jan 28, 2013 #4 As long both insulations are rated for the maximum voltage applied to the cables, in this case 277volt THHN and the most commons insulation are 600 volt rated .
As long both insulations are rated for the maximum voltage applied to the cables, in this case 277volt THHN and the most commons insulation are 600 volt rated .