So I was looking at the Siemens SND 1200A frame adjustable trip circuit breaker to be used as the main breaker for a 630A service for a small apartment complex. The continuous current rating (Ir) has a 630A trip setting available but I'm concerned about effects of the long time delay and instantaneous pickup. The lowest time delay would allow 6 x Ir , or 3780A, for 2.5 seconds, but the instantaneous pickup can reduce this further if set to the lowest setting of 1500A. Is there a certain duration you can exceed the conductor ampacity? I'm not sure where to find this in the NEC.
My particular design is for 225kVA, 3 phase overhead service @ 208Y/120V. Looking at using AL SER cable (4-4/0 with 2/0 GND) with 3 - 4/0 conductors per phase.