C cppoly Senior Member Location New York Apr 29, 2014 #1 Can 2 poles be used on a 3 pole breaker with the remaining 1 pole not used / unconnected to any conductors?
Can 2 poles be used on a 3 pole breaker with the remaining 1 pole not used / unconnected to any conductors?
480sparky Senior Member Location Iowegia Apr 29, 2014 #3 I'll even venture to say you can use just ONE pole. Better yet, it's legal to use NONE of them.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Apr 29, 2014 #4 Yes you can use 2 poles of a 3 pole breaker although it may raise the eyes of an inspector.
C cppoly Senior Member Location New York Apr 29, 2014 #5 Thanks. I couldn't find anywhere where it wasn't allowed. The conductors would still be protected in accordance with their ampacity. Figured article 240 would have been the place to not allow it.
Thanks. I couldn't find anywhere where it wasn't allowed. The conductors would still be protected in accordance with their ampacity. Figured article 240 would have been the place to not allow it.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Apr 29, 2014 #6 Can and do.