Then question becomes-is it rated for DB. Just my .0001%
Never said it was!! But, who’s to say the conduit is to standard. I’m sure most RMC "today" has the zinc coating, or suitable for DB installs. Just saying, “why trust it!”Does it have to be?
I see no such requirement in 250.
Because the code says you can and because ground rods are next to worthless no matter what they are made out of.... Just saying, ?why trust it!?
Because the code says you can and because ground rods are next to worthless no matter what they are made out of.
Never said it was!! But, who?s to say the conduit is to standard. I?m sure most RMC "today" has the zinc coating, or suitable for DB installs. Just saying, ?why trust it!?
(5) Rod and Pipe Electrodes. Rod and pipe electrodes
shall not be less than 2.44 m (8 ft) in length and shall
consist of the following materials.
(a) Grounding electrodes of pipe or conduit shall not
be smaller than metric designator 21 (trade size 3⁄4) and,
where of steel, shall have the outer surface galvanized or
otherwise metal-coated for corrosion protection.
Most copper is tubing and not pipe and would not be permitted as a grounding electrode. The same for EMT...it is not conduit or pipe, it is tubing. This comment only applies to the provisions of 250.52(A)(5)I am wondering why 3/4" copper pipe is OK to be used as an electrode. Just a stick of 3/4" pipe not the water supply.
Or how about a stick of 3/4" EMT?