P Pedro Roman Member Location Puerto Rico Occupation Solar QA Inspector Aug 19, 2020 #1 I’m having confusion in finding the right answer between 2017 NEC 314.16(C)(2) and 314.28, specifically 314.28(A)(2).
I’m having confusion in finding the right answer between 2017 NEC 314.16(C)(2) and 314.28, specifically 314.28(A)(2).
C Carultch Senior Member Location Massachusetts Aug 19, 2020 #2 Technically yes. Splicing and tapping is permitted in conduit bodies, just like it is within enclosures. Practically, good luck finding enough space inside the body to do it.
Technically yes. Splicing and tapping is permitted in conduit bodies, just like it is within enclosures. Practically, good luck finding enough space inside the body to do it.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 19, 2020 #3 314.16 should apply, but the volumes of the conductors in Table 314.16(B) stop at 6 AWG.