What's wrong with this picture? What if I go right to cable tray with no conduit? How long do the 2-per-Ø conductors have to be before I can splice them?View attachment Ampacity Test.jpg
The conductor does not have a different rating. The termination does.What's wrong with this picture? What if I go right to cable tray with no conduit? How long do the 2-per-Ø conductors have to be before I can splice them?View attachment 2557579
Fair enough. But how far apart do the terminations have to be? If one termination is operating at 45°C rise over 30°C ambient, and the other end of the wire is operating at 60°C rise, there will be heat transfer from higher to lower temperature. What's to keep the 75° lug from being a heat sink for the 90° H-tap? It seems like cable length ought to matter. Is there anything in the code about this?The conductor does not have a different rating. The termination does.
First of all, the Code itself makes no allowances at all for heat sinking of a termination through the attached wire(s).Fair enough. But how far apart do the terminations have to be? If one termination is operating at 45°C rise over 30°C ambient, and the other end of the wire is operating at 60°C rise, there will be heat transfer from higher to lower temperature. What's to keep the 75° lug from being a heat sink for the 90° H-tap? It seems like cable length ought to matter. Is there anything in the code about this?