We installed this Polyphaser Box along with an aluminum conduit running to a metal raceway on the Roof.
The conduit will contain RF cable for antennas.
We learned after the fact that the Conduit must be bonded at either side.
(this is for lightning protection reasons and not electrical reasons)
Its a bit too late to put in Grounding Bushings on either side of the Conduit,
Is there anyway we can bond the conduit on each end without using Grounding Bushings?
Even though this is Lightning protection, does the NEC Code ststill apply?
Thank you in Advance
The conduit will contain RF cable for antennas.
We learned after the fact that the Conduit must be bonded at either side.
(this is for lightning protection reasons and not electrical reasons)
Its a bit too late to put in Grounding Bushings on either side of the Conduit,
Is there anyway we can bond the conduit on each end without using Grounding Bushings?
Even though this is Lightning protection, does the NEC Code ststill apply?
Thank you in Advance