Can a NEMA 3R safety switch be used indoors?

Status
Not open for further replies.

PeteSki

New member
NEMA 250 rates a 3R device for indoor and outdoor use. However, NEC paragraph 110.28 and Table 110.28 do not acknowledge NEMA 3R devices for indoor use. Also, the Schneider Electric FAQ page says yes. Does any one know why the NEC does not recognize NEMA 3R devices for indoor use?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Table 110.28 does not state that NEMA 3R enclosures are not suitable for indoor use, it just states that NEMA 3R enclosures are suitable for outdoor use.

You can use a 3R enclosure indoors without any problems.

Chris
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
NEMA 250 rates a 3R device for indoor and outdoor use. However, NEC paragraph 110.28 and Table 110.28 do not acknowledge NEMA 3R devices for indoor use. Also, the Schneider Electric FAQ page says yes. Does any one know why the NEC does not recognize NEMA 3R devices for indoor use?

I think if you look closely, a type 3R enclosure is also a type 1 enclosure, much like many type 4 enclsoures are also type 12.
 