busman
Senior Member
- Location
- Northern Virginia
- Occupation
- Master Electrician / Electrical Engineer
I have installed quite a few of the Generac packaged standby generators for residential use. I have a situation where the Gas Meter is on the opposite corner of a large house from the service panel about 80 feet separating. Since these units use an awful lot of NG, they should be mounted close to the meter. The generator unit comes with a 30 foot whip in Greenfield with 2-#6 for ungrounded, 1 #8 grounded and 1 #10 EGC plus four control conductors that appear to be about 18 guage.
The question is: am I violating the code by replacing this whip with appropriately sized conductors in a conduit run. I would think that the generator and the transfer switch are each listed separately and that the whips are provided as a convenience, but are not required to be used. Is this a reasonable interpretation?
Thanks,
Mark
The question is: am I violating the code by replacing this whip with appropriately sized conductors in a conduit run. I would think that the generator and the transfer switch are each listed separately and that the whips are provided as a convenience, but are not required to be used. Is this a reasonable interpretation?