I have a couple Siemens AFCI combination breakers that I got a few years ago.Are they compatible in a GE Panel?
Well sort of. You can find other products out there like meter-mains and power pedestals and power outlet assemblies by Milbank or Midwest or possibly others that will have branch breaker spaces and will list various breakers such as Siemens, Eaton BR, GE and Square D Homeline as acceptable breakers to install in them.They may fit but they aren't listed for anything but a Siemens or Murray panel.
OP specifically asked about a GE panel.Well sort of. You can find other products out there like meter-mains and power pedestals and power outlet assemblies by Milbank or Midwest or possibly others that will have branch breaker spaces and will list various breakers such as Siemens, Eaton BR, GE and Square D Homeline as acceptable breakers to install in them.
That would make no difference in the OP's question.Combination or dual function? There is a difference.
I should of worded it differently, but wanted to make a point about the difference between the two typesThat would make no difference in the OP's question.
They may fit but they aren't listed for anything but a Siemens or Murray panel.
New GEs don't have GFCI while others do: https://forums.mikeholt.com/threads/new-ge-afci.77941/They fit. But on opening the panel I found the 2 breakers I wanted to replace were connected to a NM 12/3 with a shared neutral. Only GE AFCI breakers work with shared neutrals. Siemens trip.
Technically it is GFPE level protection. If it were GFCI level protection they are calling them dual function breakers. And yes GE has passed listing requirements without using any GFPE in their units.New GEs don't have GFCI while others do: https://forums.mikeholt.com/threads/new-ge-afci.77941/
Yes, I mis-worded that. Do you know if they set GFPE at 30ma or something else?Technically it is GFPE level protection. If it were GFCI level protection they are calling them dual function breakers. And yes GE has passed listing requirements without using any GFPE in their units.
I got off on a tangent. Siemens, CH, and SqD all make 2 pole AFCI breakers to cover the shared neutral case. Dual function 2 pole are still MIA.They fit. But on opening the panel I found the 2 breakers I wanted to replace were connected to a NM 12/3 with a shared neutral. Only GE AFCI breakers work with shared neutrals. Siemens trip.
I don't know for certain but I believe 30mA is what is used.Yes, I mis-worded that. Do you know if they set GFPE at 30ma or something else?