Hello all, this is my first post on this forum. I tried searching for this question but did not find a thread answering my particular question.
Anyways, on with the question:
I have a lighting outlet calling for a single pole stack switch (obviously one strap/yoke/device, whatever you want to call it), but the 2 lighting locations being controlled by each switch originate from different circuits (single gang box - yes, box fill is good). I know I need to break the line side tab, keep neutrals separate, and identify conductors in the box, but NEC article 210.7 seems to indicate the disconnecting means for these circuits must disconnect both circuits simultaneously because of this particular outlet.
The code states "Where two or more branch circuits supply devices ... on the same yoke or mounting strap, a means to simultaneously disconnect the ungrounded supply conductors shall be provided at the point at which the branch circuits originate." (2020 NEC Article 210.7)
To me this means the circuit breakers controlling these circuits must be controlled by a two pole breaker even though this is not intended to be a 240/208V application. Am I correct? Do I need to re-organize the whole panel to put the circuit breakers right next to each other so I can use a 2 pole breaker?
Anyways, on with the question:
I have a lighting outlet calling for a single pole stack switch (obviously one strap/yoke/device, whatever you want to call it), but the 2 lighting locations being controlled by each switch originate from different circuits (single gang box - yes, box fill is good). I know I need to break the line side tab, keep neutrals separate, and identify conductors in the box, but NEC article 210.7 seems to indicate the disconnecting means for these circuits must disconnect both circuits simultaneously because of this particular outlet.
The code states "Where two or more branch circuits supply devices ... on the same yoke or mounting strap, a means to simultaneously disconnect the ungrounded supply conductors shall be provided at the point at which the branch circuits originate." (2020 NEC Article 210.7)
To me this means the circuit breakers controlling these circuits must be controlled by a two pole breaker even though this is not intended to be a 240/208V application. Am I correct? Do I need to re-organize the whole panel to put the circuit breakers right next to each other so I can use a 2 pole breaker?