Can a vertical water pipe run inside a wall that is being use as a surface mounted electrical panel?

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
If you have a surface mounted panel (that meets its clearance 3' feet and 30Inches sides and nothing above it), can you have water pipe running in the wall directly behind it?

Thank you,
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes it can be behind it or even right next to it, it just cannot be in the dedicated equipment space or the working space.
 