The code is clear in that the calculated load on a circuit shall not exceed the circuit's maximum capacity, but does the code allow the actual total connected load to exceed the circuit's maximum capacity? For instance, the calculated load on a 20 amp 120 volt branch circuit with 13 general duplex receptacles in a commercial office is 2340 VA @ 180 VA per receptacle and is within the circuit's maximum capacity of 2400 VA. Plugged into the same circuit is a number of small office appliances such as printers, a copy machine, computers, desk calculators, battery chargers, fax machines, typewriters, task lighting, etc. with a total connected load based on nameplate data exceeding 2400 VA. Yet, the actual recorded averaged peak demand over a one week period is less than 50% of the circuit's capacity. This is owing to the fact that nameplate data represent maximum values and that many office appliances operate in spurts and at different times and at various loadings. Hope this example is clear. Appreciate any response. Thanks.