jtinge
Senior Member
- Location
- Hampton, VA
- Occupation
- Sr. Elec. Engr
To utilize the less restrictive wiring methods of Article 645, the six criteria listed in 645.4 of NEC 2011 have to be met. Three of those are the "room contains only listed IT equipment", "occupied by and accessible to, only those personnel needed for the maintenance and functional operation of the installed information technology equipment", and "only electrical equipment and wiring associated with the operation of the information technology room is installed in the room. Can an industrial control room having a raised floor be classified as IT room and utilize the Article 645 wiring methods if it contains industrial PLCs and other equipment in addition to listed IT equipment for control of processes or a plant and is accessible to operators of that of the non-listed equipment? It seems that many people classify these control rooms as IT rooms but the equipment and personnel accessible to that equipment don't meet the criteria of Article 645 that permits use of the less restrictive wiring methods. Is this correct? Can Article 645 be correctly utilized for industrial controls rooms as described above?