Can cables pass through rated walls without conduit sleeves?

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
Ever see cables passing through rated walls with fire stopping foam spray? Don't these need to be in a conduit sleeve for protection?
 
MC cables are typically rated for penetration through fire rated partitions up to 2 hours without sleeves.
 
Ever see cables passing through rated walls with fire stopping foam spray? Don't these need to be in a conduit sleeve for protection?

By protection you mean protection against physical damage or protection against fire spreading to other side?
 
By protection you mean protection against physical damage or protection against fire spreading to other side?

Protection against physical damage, are cables protected by passing through a core through a wall without a sleeve and simply packed with fire stopping material?
 
Protection against physical damage, are cables protected by passing through a core through a wall without a sleeve and simply packed with fire stopping material?

IMO, that depends how you interpret "physical protection". I know there are sleeves that will protect and provide the fire putty.
 
Protection against physical damage, are cables protected by passing through a core through a wall without a sleeve and simply packed with fire stopping material?

There are a gazillion (well, actually about 300) FM methods for penetrating a wall and every firestop product will include or point you to the literature displaying the methods for which their product is approved. I poked around the 3M site and found this. It will do what you want but it is limited to 1 or 2 hour rating, plus you'll have to dig up some of the additional information on the exact construction of the wall.
 