- Milton, WV
- Occupation
- Electrical Engineer
Hello! Long time listener, first time caller... I have a client who wants to run electrically heat traced tubing inside a 4" RGS (rigid galvanized steel) conduit underground. I've never done this before, and I've never heard of it being done before. I have concerns - mainly heat dissipation:
1) I understand that the point of electrically heat traced tubing is to use resistive heating as a heat source - and that it [the EHT's insulation] should be able to withstand a certain degree of heat, but I'm concerned about it overheating because it is inside conduit with nowhere for the heat to go - except dissipation through the conduit itself.
2) I'm concerned that with the conduit being buried, that will make it even more difficult to dissipate heat.
I read through NEC Article 427: Fixed Electric Heating Equipment for Pipelines and Vessels, and I didn't see anything relating to running electric heat trace (or electrically heat traced tubing) in conduit.
A little background info... I work for a company that designs metering and regulation skids for the natural gas industry. These skids are typically 50 to 100 feet from an RTU (remote terminal unit - aka PLC, SCADA, etc) / EGM (Electronic Gas Monitoring) building where the GC (gas chromatograph) is located. Samples of the gas from the pipelines are taken with a Genie probe inside of a Pony Box. From the Pony Box to the Mustang P53 panel and from there to the GC, we run electrically heat traced tubing to keep the gas warm - so that the gas doesn't condense and drop out as liquid on its way to the GC. The EHT-tubing is buried between the skid and the RTU building. I've never given that part much thought until today when a client asked if they could run TWO EHT-tubings together in a single 4" conduit. I told the client that I wasn't even sure that, by code, you can run any EHT inside a conduit - much less two! ...So that brings me to running two EHT together in one conduit. Is that allowed? My understanding of electric heat trace (EHT) is that you're not supposed to run multiple EHT cables together / on top of each other - I suppose because they'll melt each other (?) from the combined heat. With regular EHT, if you have to cross them, you cross them at right angles - again, I suppose to 1) cancel magnetic fields / induced currents and 2) minimize contact.
Any ideas on this matter?
Thanks!
Aaron Ward
1) I understand that the point of electrically heat traced tubing is to use resistive heating as a heat source - and that it [the EHT's insulation] should be able to withstand a certain degree of heat, but I'm concerned about it overheating because it is inside conduit with nowhere for the heat to go - except dissipation through the conduit itself.
2) I'm concerned that with the conduit being buried, that will make it even more difficult to dissipate heat.
I read through NEC Article 427: Fixed Electric Heating Equipment for Pipelines and Vessels, and I didn't see anything relating to running electric heat trace (or electrically heat traced tubing) in conduit.
A little background info... I work for a company that designs metering and regulation skids for the natural gas industry. These skids are typically 50 to 100 feet from an RTU (remote terminal unit - aka PLC, SCADA, etc) / EGM (Electronic Gas Monitoring) building where the GC (gas chromatograph) is located. Samples of the gas from the pipelines are taken with a Genie probe inside of a Pony Box. From the Pony Box to the Mustang P53 panel and from there to the GC, we run electrically heat traced tubing to keep the gas warm - so that the gas doesn't condense and drop out as liquid on its way to the GC. The EHT-tubing is buried between the skid and the RTU building. I've never given that part much thought until today when a client asked if they could run TWO EHT-tubings together in a single 4" conduit. I told the client that I wasn't even sure that, by code, you can run any EHT inside a conduit - much less two! ...So that brings me to running two EHT together in one conduit. Is that allowed? My understanding of electric heat trace (EHT) is that you're not supposed to run multiple EHT cables together / on top of each other - I suppose because they'll melt each other (?) from the combined heat. With regular EHT, if you have to cross them, you cross them at right angles - again, I suppose to 1) cancel magnetic fields / induced currents and 2) minimize contact.
Any ideas on this matter?
Thanks!
Aaron Ward