Can I apply 240.4(B) to conductors to wireway?

Status
Not open for further replies.
As I read 240.4(B) I see an overcurrent protective device ahead of the conductors. Does the conductors coming in have an overcurrent protective device ahead of them?
 
For the conductors identified, assuming there is no over-current protection ahead of them and assuming they are service conductors, the correct size be be derived form 230.42 based on a load calculation.
 
The OP's question, in looking for an allowance in 240.4 for protection of the conductors in question, reveals 240.4 has none. As such 240.4 conflicts with the allowance in 230.90(A) Exception 3. Looks like we need a 2029 PI for a new section 240.4(I) that references 230.90(A) Exception 3--there weren't any such PIs submitted for 2026.

Cheers, Wayne
 
Last edited:
Are you asking if you can use an 800A OCPD ahead of the two meters, and if the (2) sets of 500mcm will be acceptable under 240.4(B) because that overcurrent would be 800A? And is your intent to come off of that 800A OCPD with the conductors shown to the meters? I would say, and anyone please correct me if I am wrong, if your load calculations permits you to use an 800A OCPD, you should be permitted to abide by 240.4(B).
 
Are you asking if you can use an 800A OCPD ahead of the two meters, and if the (2) sets of 500mcm will be acceptable under 240.4(B) because that overcurrent would be 800A? And is your intent to come off of that 800A OCPD with the conductors shown to the meters? I would say, and anyone please correct me if I am wrong, if your load calculations permits you to use an 800A OCPD, you should be permitted to abide by 240.4(B).

The problem is there is no overcurrent protective device before those service cables. 240.4(B), imo seems to indicate that we can upsize the overcurrent protective device protecting the conductors...
 