Factory installed main breaker may not have additional information on any labels related to changing that main breaker. They often only have information on branch breakers allowed.If the panel is rated 125 amps and allows the install of a 125 amp main then it is fine. The panel info should state what breakers would be compliant
Are you the utility then? You can't "upgrade the service wires" unless you are the utility, and if not they don't want you touching their side of the service. If they have provided a 100A service drop, you can't just arbitrarily increase that. They have to be consulted first.I have a 100 amp service meter/ main with a factory installed 100 CB. The buss bar is rated 125 amp. Is it OK to install a 125 amp main CB? I will upgrade the service wires to #2 Copper.
Are you the utility then? You can't "upgrade the service wires" unless you are the utility, and if not they don't want you touching their side of the service. If they have provided a 100A service drop, you can't just arbitrarily increase that. They have to be consulted first.
Our POCOs are very responsive but I highly doubt they would change the size of their service drop solely because I upgraded a 100 to a 125. Maybe if I changed it to a 200 and told them we changed to electric heat. We are responsible from POA on in.
Are you the utility then? You can't "upgrade the service wires" unless you are the utility, and if not they don't want you touching their side of the service. If they have provided a 100A service drop, you can't just arbitrarily increase that. They have to be consulted first.
In doing so you will have increased the size of the service, which you should not do without consulting the utility. You don't know what size conductors are on their side of the meter, and most POCO's will have a problem with your breaking the seal on their meter can. You could be looking at a substantial fine for doing that.I have a 100 amp service meter/ main with a factory installed 100 CB. The buss bar is rated 125 amp. Is it OK to install a 125 amp main CB? I will upgrade the service wires to #2 Copper.
I would have assumed he meant the conductors on the customer's side of the service point.
I would say it should be OK to put a 125 amp breaker in it then.My mistake. I should have said Service entrance conductors.
Of course I do not change the service drop wires. That is poco job.
And I would be doing this with permit and poco permission.
The specs on panel say 125 amp rating. But do not say it is ok to remove factory 100 amp breaker and replace with 125. That is why I am asking the question.
My mistake. I should have said Service entrance conductors.
Of course I do not change the service drop wires. That is poco job.
And I would be doing this with permit and poco permission.
The specs on panel say 125 amp rating. But do not say it is ok to remove factory 100 amp breaker and replace with 125. That is why I am asking the question.
In general, replacing a panel's OCPD is OK if it is accommodated by the design of the panel and it doesn't result in the OCPD being higher rated than the panel busbars.
Problem may be somewhat a technicality though. Some panels with factory installed 100 amp main may only say 100 amps on any labeling, yet are built with same bus assembly as some that are marked as 125 amps.