Does anyone see why I can Not do this.I want to add one 8' strip of base board 240v I want to use the ac air handler circuit its 15 amp and is only used for ac can I do this by code?
Assuming normal density, it will be a 2 kW heater and at 240 volts, that is only a bit over 8 amperes. Add the required 25% for continuous load and you are shy of 11 amperes . . . no problem. :smile:SiddMartin said:. . . Is the 15 A ckt large enough for the contin. load of the heater? . .
Agree, I woud think that would just be a good install. :smile:480sparky said:. . . install a DPDT switch to toggle between the two. Then there's no chance both loads can be on at the same time.
480sparky said:, install a DPDT switch to toggle between the two. Then there's no chance both loads can be on at the same time.
I know things have changed a bit since I hung up my tool belt in 1979 but a DPDT snap switch can't be that expensive . . . can it? :-?buckofdurham said:. . . The switch is about $45.00
goldstar said:. . . With respect to the NEC and receptacles over the BB heater, does the NEC distinguish between the BB heating unit having an electric or hydronic element ?
Jerseydaze said:what about this the Ac system is fed by a 40 amp sub panel if I add a circuit out of that panel for the heat is it up to code because its heat and ac .If you ran Ac and baseboard you would over load the sub panel
charlie said:I know things have changed a bit since I hung up my tool belt in 1979 but a DPDT snap switch can't be that expensive . . . can it? :-?