RossS
Member
- Location
- Research Triangle, NC USA
- Occupation
- Electrical engineer
I have an interesting challenge. I have a college classroom that is being converted to auditorium style tiered seating. Currently there are many receptacles along the side walls at standard height (~18" AFF). They are installing 5 tiers of seating, each one 4" higher than the preceding tier, so the fifth tier is going to be +20" AFF, and is going to conflict with the existing receptacles. The existing walls are old plaster and the administration doesn't want to demo any more than they absolutely have to.
If I remove any receptacle, I have to restore power to any downstream devices. Is there any scenario, any renovation technique that will allow me to remove the existing receptacle, cover up the outlet box and render it inaccessible? If I pull out the conductors from both ends, and replace with continuous conductors passing straight through without splicing, does the outlet box still have to be accessible? I was thinking there was an exception along those lines, but I can't seem to find it now.
If I remove any receptacle, I have to restore power to any downstream devices. Is there any scenario, any renovation technique that will allow me to remove the existing receptacle, cover up the outlet box and render it inaccessible? If I pull out the conductors from both ends, and replace with continuous conductors passing straight through without splicing, does the outlet box still have to be accessible? I was thinking there was an exception along those lines, but I can't seem to find it now.