I just wanted to thank you again so much for taking the time to look at my situation and providing me great advice. The first one line picture is what is existing on the structure right now. The second one line picture is what I’m proposing I do to make it a safer system. The following pictures are provided for insight so you can see what I’m referring to in the one lines… my questions for you are:
1- per Nec am I allowed to remove the added breakers at the double throw, set a new enclosure and use 230.46 to tap or splice on the line side of service conductors?
2- if I am allowed to use 230.46 to make two or splice on the line side of service conductors. Am I allowed to have two separate service disconnects on one structure? I would have the 3phase 200a 240 high leg service disconnect, and the 120/240 200a service disconnect. If I read correctly I would have to implant 250.64(d)(1)
If I’m not allowed to have the two service disconnects on one structure my plan is to land a 200a 3ph service disconnect in place of term box and then feed a 200a mpd from service disconect. Mpd would then feed the 3 existing panels and I would have to get a egc installed in raceway and isolate at all panels except for service disconnect.
As far as grounding and bonding goes. wherever I have my service disconnect I need to run #4 gec to metal water pipe, then bond to building the steel using #2 and #6 to ground rods sized on 250.102 (c) (1) ?
1- per Nec am I allowed to remove the added breakers at the double throw, set a new enclosure and use 230.46 to tap or splice on the line side of service conductors?
2- if I am allowed to use 230.46 to make two or splice on the line side of service conductors. Am I allowed to have two separate service disconnects on one structure? I would have the 3phase 200a 240 high leg service disconnect, and the 120/240 200a service disconnect. If I read correctly I would have to implant 250.64(d)(1)
If I’m not allowed to have the two service disconnects on one structure my plan is to land a 200a 3ph service disconnect in place of term box and then feed a 200a mpd from service disconect. Mpd would then feed the 3 existing panels and I would have to get a egc installed in raceway and isolate at all panels except for service disconnect.
As far as grounding and bonding goes. wherever I have my service disconnect I need to run #4 gec to metal water pipe, then bond to building the steel using #2 and #6 to ground rods sized on 250.102 (c) (1) ?
Attachments
-
0E1C10D8-EB04-423B-8D30-EB16171001DE.jpeg308.4 KB · Views: 18
-
50BFA5AB-F54A-4035-8077-1579EED5B9B8.jpeg285.4 KB · Views: 18
-
8C4C8F66-78D9-4FDE-B827-9A673BD66F93.jpeg248.2 KB · Views: 19
-
B0B53663-BDFB-41F6-AF63-623F1928879F.jpeg512.2 KB · Views: 16
-
7CE7BEE0-2AC2-4449-8952-31010D71E27D.jpeg346.8 KB · Views: 17
-
39CEADE7-1644-49E0-8BB2-8E53265CAF48.jpeg503.8 KB · Views: 17
-
9CA4FAFF-6041-47E9-9996-C49A340FCADD.jpeg361.9 KB · Views: 16
-
8711760F-3F67-42F5-BA37-7EBB1CA39B37.jpeg395.5 KB · Views: 17
-
2AFDE182-6A7F-414D-BE97-DA1872C8A433.jpeg384.4 KB · Views: 17
-
DEB0F7F2-4F6F-4A41-8AB1-2081A432D183.jpeg925.6 KB · Views: 16