Can I move the neutral and/or ground for the generator inlet?

Status
Not open for further replies.

Bsparky

New User
Location
California
Occupation
Health Care
Hello all,

We have a new 200 amp service, with a new meter box and service disconnect on the exterior of the house. Directly behind the meter box is a new larger 40 spot sub-panel.

We want to install a generator inlet because we live in an area that may lose power for many hours. We have gas appliances, including furnace, so a 30 amp inlet should be enough for a few hours running lights and refrigerators.

The main meter box and service disconnect cannot have an interlock attached the seimens manual. The sub-panel has a main breaker disconnect instead of a lug-load center, and that is where the interlock will be placed.

My question is regarding the ground and neutral coming from the generator inlet. The generator will have a floating neutral, BTW. Sub-panel the neural and ground are NOT bonded.

Can the neutral and ground from the inlet box be moved from the sub panel to the main disconnect bonded neutral/ground bar? The main feeder conductors are running through rigid conduit from the main disconnect panel to the sub panel but is only 1-1/2 inch and there are already. It would probably be over 40% to add 4 more THHN 8awg wires through that raceway. I know 10 awg can work for 30amp, but I had a bunch of 8 awg sitting around.

The picture included is what I imaging the wiring looking like, the dashed line being the neutral.

Many thanks.

Picture of the wiring
 
Please try diychatroom.com

This site is designed for:

  • Electrical Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.
 
Status
Not open for further replies.
Top