J JPoint New User Location USA Occupation Electrician Jun 29, 2020 #1 Can I run emergency circuits thru the same gutter with normal power circuits if I seperate the circuits with dividers?
Can I run emergency circuits thru the same gutter with normal power circuits if I seperate the circuits with dividers?
roger Moderator Staff member Location Fl Occupation Retired Electrician Jun 29, 2020 #2 If the divider effectively creates two individual sections yes you can. Wire duct manufactures have factory made dividers for this reason. Roger
If the divider effectively creates two individual sections yes you can. Wire duct manufactures have factory made dividers for this reason. Roger