I have a 4 wire 240V circuit powering an indoor pool heater, protected by a 50A GFCI breaker in the main panel. Neutral isn't used by the heater, but it's present in the disconnect junction box near the heater.
Question: Can I use one of the hots plus the neutral to create a 120V circuit? I am aware that I would need to install a 15 or 20A circuit breaker for the 120V circuit in a junction box/subpanel near the heater.
a) Is this to code?
b) Will it trip the GFCI breaker due to the current imbalance created between the two legs of the 240V circuit?
Question: Can I use one of the hots plus the neutral to create a 120V circuit? I am aware that I would need to install a 15 or 20A circuit breaker for the 120V circuit in a junction box/subpanel near the heater.
a) Is this to code?
b) Will it trip the GFCI breaker due to the current imbalance created between the two legs of the 240V circuit?