zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
NEC 230.95 requires that "Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. "
For example, we have a 3000A main service breaker for 480Y/277V 3ph 4w service. Can I specify GFCI breaker instead GFPE? GFCI has lower threshold amps and provide more protection to human that GFPE can't provide.
Thank you,
For example, we have a 3000A main service breaker for 480Y/277V 3ph 4w service. Can I specify GFCI breaker instead GFPE? GFCI has lower threshold amps and provide more protection to human that GFPE can't provide.
Thank you,